Mr. Serious
- Oklahoma, USA
- Electrical Contractor
My job site is a convenience store remodel halfway between McAlester and Muskogee, Oklahoma, and I have a couple of things that a licensed PE could help with. This is the first significant job I've taken on as a contractor, so I'd appreciate some recommendations or assistance finding someone who could do these two things:
- On the print there is a note saying "The electrical power and distribution system, including the grounding system, shall be completely tested prior to the completion of the project." This seems somewhat vague to me, and the owner and/or architect are not likely to hold me to any particular standard of testing, but it seems I could at least try to get some measurements of the resistance to ground of the electrodes and perhaps some similar measurements for the feeder conductors.
- Because of a mistake on the initial equipment order that I didn't catch in time for them to re-order the correct size breaker, I ended up with one breaker with settable trip points. It's a breaker with frame size that normally only comes in 400A or greater amp ratings, but we needed it to be 225A, so they supplied me with an ABB SACE Tmax XT5 breaker with an Ekip Dip LS/I trip unit. I did a coordination study myself and set the switches to what I believe is correct, but I would like a licensed PE to verify my settings and perform the initial test of the breaker that is required by the trip unit instructions. I think the breaker is supposed to connect to a computer running ABB's software to perform the initial test.