Loose Conductors in a box

Status
Not open for further replies.
I thought I have read in the NEC somewhere that all conductors located in a device box shall be terminated. I cannot seem to find it now.

The problem I have is:

I don't know if a peice of equipment is 120 or 208 single phase. My first thought was to pull an extra hot and cap it if the unit is only 120V. But I thought I read you cannot do this.

Can someone please point out an NEC artical that will or or will not allow you to do this.

Thanks in advance
Matt
 
mbergheger said:
II don't know if a peice of equipment is 120 or 208 single phase. My first thought was to pull an extra hot and cap it if the unit is only 120V. But I thought I read you cannot do this.

Sure you can. There is no code prohibiting it.
 
mbergheger said:
I thought I have read in the NEC somewhere that all conductors located in a device box shall be terminated. I cannot seem to find it now.

The problem I have is:

I don't know if a peice of equipment is 120 or 208 single phase. My first thought was to pull an extra hot and cap it if the unit is only 120V. But I thought I read you cannot do this.

Can someone please point out an NEC artical that will or or will not allow you to do this.

Thanks in advance
Matt

There is no article that says you cannot have an extra wire in a JB. It is terminated when you put a wirenut on the end. :wink:
 
agree.gif
 