Thank you for your assessment of my knowledge, it has the same value to me as what I paid for that assessment230722-21212 EDT
don_resqcapt22:
Your understanding of multiple phases is incorrect. Your approach would flunk you in an elementary course in a basic college AC circuit class.
Do you have available a scope with at least two vertical channels, and a single shot time based channel. The horizontal channel would be a linear sweep vs time, and the vertical channels would be the signals you want to look at vs time.
The horizontal channel is triggered by a signal. This trigger is usually selected from one of the vertical channels, the AC line, or an external source. Also the horizontal sweep can come from an external signal, an internal sweep generator, and the internal linear time sweep can be repetitive, synced or free running, or single shot. single shot would be triggered from some source.
Best to operate under battery mode, or open the EGC path in the AC power cord.
For 60 Hz tests as a starter it is good to use 2 mS or 5 mS time base per major division. Use 10X probes if you are going to look at 120 signals.
Connect the scope common to the center tap of your source voltage.
Label the transformer output terminals, the hot ends, as A and B, and the center tap as N.
Connect the scope common to N.
Connect scope external sync to A with appropriate attenuation. This makes the scope sync common to Channel A. Connect scope probe 1 to A, and adjust sync phasing so that left most half sine wave, relative to sync point, is positive on the screen. Some scopes allow you to adjust the sync start point to the right of the left side of the display.
If you can do this report back.
.