As a general rule , rectifiers (ie- your power supplies) wired with 480/277 3ph will require an isolated / dedicated N leg along with a ground.
If you only have 4 conductors, you probably just found your problem.
I will assume the power supply tech specs call out 480/277 with N and ground.
If you have a back up generator that kicks in during your power outtage, then the genset also needs to have dedicated N legs as well as ground wired back to the transfer switch.
At your plant, you have the the main power room and in your switch gear where your feeder breakers are, there is a common ground bar.
Here is what you need to do.............
open the unit , or research the factory spec wiring. I highly suggest you observe the pretences on 230v engineering because many german makers are very savy with US wiring but also are polluted with those not really understanding the need of a N and a G leg on the input to rectifiers.
Since you did not mention a back up genset kicking on, we can ignore that option.
Your primary problem is getting the rectifiers to fire back up and as a result of the power loss. The inrush isnt really the issue here but the amount of potential on the rectifier ground upon startup. DC is a totally different ball game and you need to have experienced people who know the science of integrating DC into an 3phase AC infrustructure.
Ill bet you will find that your N and G leg are coupled together somewhere on the input side of the rectifiers close to the source.
Ground is not "GROUND", You can make ground any potential you want. "GROUND" is a REFERENCE VOLTATGE. If your rectifier ref ground needs to be zero =-1% tolerance, then make it so.
in short, you need 5 dedicated wires coming to the rectifiers. the inrush will not effect your rectifiers any longer once you do this.
If you only have 4 conductors, you probably just found your problem.
I will assume the power supply tech specs call out 480/277 with N and ground.
If you have a back up generator that kicks in during your power outtage, then the genset also needs to have dedicated N legs as well as ground wired back to the transfer switch.
At your plant, you have the the main power room and in your switch gear where your feeder breakers are, there is a common ground bar.
Here is what you need to do.............
open the unit , or research the factory spec wiring. I highly suggest you observe the pretences on 230v engineering because many german makers are very savy with US wiring but also are polluted with those not really understanding the need of a N and a G leg on the input to rectifiers.
Since you did not mention a back up genset kicking on, we can ignore that option.
Your primary problem is getting the rectifiers to fire back up and as a result of the power loss. The inrush isnt really the issue here but the amount of potential on the rectifier ground upon startup. DC is a totally different ball game and you need to have experienced people who know the science of integrating DC into an 3phase AC infrustructure.
Ill bet you will find that your N and G leg are coupled together somewhere on the input side of the rectifiers close to the source.
Ground is not "GROUND", You can make ground any potential you want. "GROUND" is a REFERENCE VOLTATGE. If your rectifier ref ground needs to be zero =-1% tolerance, then make it so.
in short, you need 5 dedicated wires coming to the rectifiers. the inrush will not effect your rectifiers any longer once you do this.