I have a newly completed large commercial building, 2500A 480/277v 3 phase service with 400kw 480/277v 3 phase diesel backup generator.
My issue started with a call from AV department complaining of AV equipment, laptops/their power supplies, thinkpad batteries, and some network equipment being “burned up”.
First visit we check receps/panels for the area and find no issue. Good voltage L-N L-G and no voltage N-G. Can’t find any issue that would cause their problem so we let it go thinking maybe it was a weird fluke.
Get another call couple weeks later multiple computer monitors have had their hdmi ports fried. Monitors all still work fine with dvi connection just not hdmi. Again we have all good voltages nothing out of the ordinary voltage wise. But while amp clamping taking readings in a panel I find we have almost 5 amps on the panels ground and no continuity neutral to ground.
Ok so we have a lost feeder neutral I think right? However I still have normal voltages L-N and still have a load on the panels main neutral. I go to the panel feeding this panel and neutral ground continuity is good, but I still have a load on ground. I go to the transformer feeding this panel to check that it’s properly bonded and it is, but I still have a load going back on GEC to the ground system.
Everything is properly bonded at MDP, generator and transformers, building steel, cold water all of that. The building has a ton of grounding, large ground busses in all electrical rooms everything is tied together ground wise, multiple ground rings all that. Majority of building is hard piped with some mc.
We’ve checked neutral connections on everything feeding to the problem panel that has lost continuity.
Is it possible to have a lost neutral but still have a load on neutral, normal L-N voltage no N-G voltage and loss of N-G continuity? And could this cause the load on our egc or is that just normal current it’s picking up from any list of things?