I don't know much about this type of transformer and would like to ask a question if i may.
What if a service is in place with a 480v corner ground and a generator is needed for what ever reason . How do you spec out the correct generator for a corner grounded system ? Will generator service know the differrence?
A few things need considered in this case. If the grounded phase happens to pass through three pole breakers for all loads, one could use a generator with a 277/480 Y output much easier as all wiring would be same for either supply.
If you have fuses in the existing system you can not put them in the grounded phase - this would be a problem with a 277/480 Y generator. You may be able to float the neutral and ground a phase and then it will be ok.