Come on and pony up some more information as the the nature of the service that your trying to apply a circuit breaker too ? :roll:
 
george lohri said:
hi where is the breaker down sizing rule thanks

You can often downsize a breaker as long as the load is not greater than the breaker capacity. More often one can upsize a breaker---
Article 240.4(B). It is really about upsizing the breaker but gives the rules for when you can. Thus it will tell you when you cannot upsize.

Art. 240.4(C) says if the OCP is over 800 amps you cannot upsize at all.
 
Dennis Alwon said:
You can often downsize a breaker as long as the load is not greater than the breaker capacity. More often one can upsize a breaker---
Article 240.4(B). It is really about upsizing the breaker but gives the rules for when you can. Thus it will tell you when you cannot upsize.

Art. 240.4(C) says if the OCP is over 800 amps you cannot upsize at all.


I would bet all of Dennis's money that the section number that Dennis posted is what the OP is referencing.
 
Pierre C Belarge said:
I would bet all of Dennis's money that the section number that Dennis posted is what the OP is referencing.

Good morning Pierre--- that was the most generous offer I heard in weeks.:grin:
 