If you are building the project, the clip can NEVER substitute for a lockable disconnect that is compliant with 110.25.I would like to ask in which cases Loto clip can substitute a disconnect next to utilization equipment.
2$ clip is less expensive than a 100 amp 3 pole disconnect
Theoretically at this point .
They are not suitable for any type of lockout but often are used to "lock" critical circuits, such as a fire alarm power supply in the on position.
Art 430 and 440 pretty much require disconnect at the equipment location.I would like to ask in which cases Loto clip can substitute a disconnect next to utilization equipment.
2$ clip is less expensive than a 100 amp 3 pole disconnect
Theoretically at this point .
If you go into an existing facility and you do follow rather strict LOTO procedures you can use these clip on devices for your LOTO purposes. They just are not recognized by NEC as a locking means in any places NEC requires a locking means.They are not suitable for any type of lockout but often are used to "lock" critical circuits, such as a fire alarm power supply in the on position.
All of the facilities that follow strict LOTO procedures, that I have worked in provide a 110.25 device on all breakers. Can't tell you how many thousands of the breaker devices that we installed in one facility.If you go into an existing facility and you do follow rather strict LOTO procedures you can use these clip on devices for your LOTO
All of the industrial facilities that I have worked in do not provide a local lock out at the motors because they use the exception to 430.102(B). However there is no such exception for Article 440 equipment.When it comes to art 430 and 440 equipment NEC pretty much requires a disconnect within sight of the equipment