I have 24 12/2 MC cables that I want to land in a panel. The top of the panel does not have enough room for all the KO's I would need to make. I was thinking I would mount a 6x6x24 wireway above the panel and connect three 1" EMT nipples between the wireway and the panel. (I calculated I can run 39 conductors in each nipple at 60% fill.) The top of the wireway should give me plenty of room for the KO's. However, I see that I will have to derate if I go over 30 CCC. If I put an end cap in the middle of the wireway (dividing it in two halves), can I then put 30 CCC in each half without derating? Alternately, can I set two 6x6x12 wireways end to end (touching) and put 30 in each without derating?