After 25 days in the field I am home! So, The Army Corps of Engineers completes the site assessments and then we get assigned the work order. Basically these temporary power generators are placed on the ground, THHN is placed on the ground and ran to a connection point. This point could be a disconnect, a meter base, or inside to buss bars in larger gear. The facilities of course are already have a bonded ground/neutral and so does the generator. So, when a ground rod is installed at the generator sometimes we get partial voltage on the grounding electrode conductor. Yes one solution would be to remove the building ground/neutral bond but that is really not feasible since the installation crew is not the de-install crew months later. The manufacturer says to install a ground rod at the generator but what if we simply did not install that ground rod? Any suggestions for these temporary generator installations?
One last note. Sometimes the engineers will direct us to connect the grounding electrode conductor from the generator to the existing ground rod and I know that that is not the correct installation.