J jjavier Member Location Maine May 25, 2017 #1 Can run dc 24 volts and communication cable (cat6) in the same conduit?
J jjavier Member Location Maine May 26, 2017 #2 dc power and com dc power and com jjavier said: Can run dc 24 volts and communication cable (cat6) in the same conduit? Click to expand... Anyone use power 24 vdc and communication together?
dc power and com dc power and com jjavier said: Can run dc 24 volts and communication cable (cat6) in the same conduit? Click to expand... Anyone use power 24 vdc and communication together?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician May 26, 2017 #3 Assuming the 24 volts is from a Class 2 power supply, the code would permit that.
P pcanning87 Member Location New York May 27, 2017 #4 I've run 24Vdc, Cat 5/6, and RS-485 together without any issues. Sent from my iPhone using Tapatalk