The reason for this email is to have your opinion regarding the importance of having low impedance to earth.
Very often, I found in the industry the requirement that a grounding electrode system should have very low resistance to earth, sometimes even approaching the magical one ohm.
I find this unreasonable under a practical and also under a theoretical point of view.
This subject is complex to analyze in its entirety, but I believe that if we restrict the subject to only grounding (without considering lightning strikes and without considering sensitive electronic equipment), we can conclude the following:
If the building has a well designed and implemented grounding system according to the NFPA publications and IEEE standards, there is no need for the grounding electrode system to have a low resistance.
If we now include lightning strikes, I believe that the subject changes. I agree that low impedance to the lightning current will help prevent side flashes from the down conductors to grounded metal equipment near it. But the NFPA 780-2000 considers that it is much more important to prevent side flashes by having frequent and excellent bonding instead of low impedance to ground. So much is this the case, that the NFPA DOES NOT REQUIRE minimum impedance neither a minimum resistance to earth for their grounding terminals. So again, you can have an excellent grounding system with grounding electrodes having high resistance to earth.
Bringing electronic sensitive equipment to the table, is more complicated, and will require possible more time that you have assigned to answer these questions. But I believe that, even when the building houses sensitive equipment, if you have a well designed grounding system and a well designed lightning protection system, the resistance or impedance to earth of the grounding electrode system is irrelevant.
Please engage in this discussion, because I believe that there is too much mystery waiting to be solved in this subject.
Ruben Corvalan
Director
CYAMSA
Very often, I found in the industry the requirement that a grounding electrode system should have very low resistance to earth, sometimes even approaching the magical one ohm.
I find this unreasonable under a practical and also under a theoretical point of view.
This subject is complex to analyze in its entirety, but I believe that if we restrict the subject to only grounding (without considering lightning strikes and without considering sensitive electronic equipment), we can conclude the following:
If the building has a well designed and implemented grounding system according to the NFPA publications and IEEE standards, there is no need for the grounding electrode system to have a low resistance.
If we now include lightning strikes, I believe that the subject changes. I agree that low impedance to the lightning current will help prevent side flashes from the down conductors to grounded metal equipment near it. But the NFPA 780-2000 considers that it is much more important to prevent side flashes by having frequent and excellent bonding instead of low impedance to ground. So much is this the case, that the NFPA DOES NOT REQUIRE minimum impedance neither a minimum resistance to earth for their grounding terminals. So again, you can have an excellent grounding system with grounding electrodes having high resistance to earth.
Bringing electronic sensitive equipment to the table, is more complicated, and will require possible more time that you have assigned to answer these questions. But I believe that, even when the building houses sensitive equipment, if you have a well designed grounding system and a well designed lightning protection system, the resistance or impedance to earth of the grounding electrode system is irrelevant.
Please engage in this discussion, because I believe that there is too much mystery waiting to be solved in this subject.
Ruben Corvalan
Director
CYAMSA