I am designing a system that will monitor points in a Class II Div 1 environment. The system is intrinsically safe and is networked, meaning that all devices are brought to a central field connection box in the classified area and then one Cat 5E cable is run back to the control panel located in a general purpose area. I have been asked to specify a direct-bury Cat5E cable jacket and to run the cable in conduit horizontally to a point near the field connection box, then drop down in open air to the field connection box. The manufacturer maintains that this installation is fine and that the cable does not need to be in conduit. My interpretation of article 250.100 and 502.30 tell me that without the rigid steel conduit connection to the threaded hubs of the field connection box, we are losing the continuity of the grounding connection to that box and therefore this installation would violate the NEC. Who's interpretation correct?
Also, I would like to know if it is OK to run IS rated low voltage cable in open air in classified, (Class II Div 1 and Div 2), areas. Article 502.10 tells me "no", but the equipment manufacturer and on site electrician say "yes".