Hi Guys:
I'm new to this forum. I'm hoping to get the real answer to this question. If any of you have seen this question postes elsewhere, I apologize for the redundancy. I'm just getting conflicting information. After watching a couple of Mike's Youtube video's, I'm feeling that I'll get a solid answer here. Here's the project;
We have to install a low voltage snow melting system on a membrane roof on a new school. There are 8 zones, each using (1) pair of #2thhn (total 16 cables) as "cold leads" from the transformer in the "control room" on the 3rd floor fed down through the floor into a plenum ceiling area on the 2nd floor where they travel accross the ceiling area through a sheetrock wall into and through another room without a plenum ceiling and then into a third room that is plenum celings. They then run up through the ceiling of the 3rd room plenum to the roof above. (I hope that's clear)
Here's where it gets funner...the lead pairs stay together as two runs of 8 cables (or 4 zones each) through the floor of the control room down to 12"x12" x4" work boxes where, once they penetrate the floor need to branch off the pairs to their respective coverage areas. The pairs stay together until they have to penatrate the 3rd room's ceiling up to the roof where they then connect to each of two ends of the element that is laid out on the roof.
Here's what we would like to do: pull each pair of #2's through (8) separate 1" FMC (steel) out to where each run ends at 4" junction boxes. The then leads split up out of the box and are run using aluminum 1/2" FMC up to where they penetrate the roof.
We don't want to use EMT because 1)of all the equipment that is already up there blocking our paths that would create a minefield of issues for bending and C) We are not allowed to remove the dropped ceiling grid which would make it alomost impossible to send 10' lengths up into the ceiling plenum area with all the obstructions. Also, we have to pull it into the greenfield because the supplier(s) only make 3 conductor MC as standard when it comes to #2thhn, AND, there's no way to get the 1000' reel of 1" MC up to the third floor of the school.
All that for the question; I understand that FMC can only be run in 6' runs when connecting to the equipment installed up in the plenum but are there a length restrictions to just running FMC through the plenum areas when not connecting to a fixture inside the plenum?
Thanks in advance for taking the time...
I'm new to this forum. I'm hoping to get the real answer to this question. If any of you have seen this question postes elsewhere, I apologize for the redundancy. I'm just getting conflicting information. After watching a couple of Mike's Youtube video's, I'm feeling that I'll get a solid answer here. Here's the project;
We have to install a low voltage snow melting system on a membrane roof on a new school. There are 8 zones, each using (1) pair of #2thhn (total 16 cables) as "cold leads" from the transformer in the "control room" on the 3rd floor fed down through the floor into a plenum ceiling area on the 2nd floor where they travel accross the ceiling area through a sheetrock wall into and through another room without a plenum ceiling and then into a third room that is plenum celings. They then run up through the ceiling of the 3rd room plenum to the roof above. (I hope that's clear)
Here's where it gets funner...the lead pairs stay together as two runs of 8 cables (or 4 zones each) through the floor of the control room down to 12"x12" x4" work boxes where, once they penetrate the floor need to branch off the pairs to their respective coverage areas. The pairs stay together until they have to penatrate the 3rd room's ceiling up to the roof where they then connect to each of two ends of the element that is laid out on the roof.
Here's what we would like to do: pull each pair of #2's through (8) separate 1" FMC (steel) out to where each run ends at 4" junction boxes. The then leads split up out of the box and are run using aluminum 1/2" FMC up to where they penetrate the roof.
We don't want to use EMT because 1)of all the equipment that is already up there blocking our paths that would create a minefield of issues for bending and C) We are not allowed to remove the dropped ceiling grid which would make it alomost impossible to send 10' lengths up into the ceiling plenum area with all the obstructions. Also, we have to pull it into the greenfield because the supplier(s) only make 3 conductor MC as standard when it comes to #2thhn, AND, there's no way to get the 1000' reel of 1" MC up to the third floor of the school.
All that for the question; I understand that FMC can only be run in 6' runs when connecting to the equipment installed up in the plenum but are there a length restrictions to just running FMC through the plenum areas when not connecting to a fixture inside the plenum?
Thanks in advance for taking the time...