There's not one, it's just a preference.
I am wondering now if it is ok to run plumbing and low voltage in the same hole
If you have two cables in the same hole then no separation is required. The 2" dimension does not apply to power and "low voltage" cables.
Please see 725.136 (NEC 2011) Separation from Electric Light, Power, Class 1,
Non-Power-Limited Fire Alarm Circuit Conductors, and
Medium-Power Network-Powered Broadband Communications Cables
Look at (I). The OP's description of this "installation" doesn't appear to meet any of the exceptions (B) through (H). And before you jump on the liberal use of the word "conductors" in this section, note that (A) says "Cables and conductors..."
Are you saying that conductors and cables are the same thing?
Are you saying that conductors and cables are the same thing?
None of this applies to a hole in a stud though.What I'm saying is that the NEC is applying this criterion to BOTH cables and conductors.
725.136
(A) General. Cables and conductors of Class 2 and Class 3
circuits shall not be placed in any cable, cable tray, compart-
ment, enclosure, manhole, outlet box, device box, raceway,
or similar fitting with conductors of electric light, power,
Class 1, non?power-limited fire alarm circuits, and medium-
power network-powered broadband communications cir-
cuits unless permitted by 725.136(B) through (I).
None of this applies to a hole in a stud though.
Its an industry standard of course, not to install low voltage wiring in the same drilled hole through a wooden residential stud that contains standard electrical 120volt wiring. I would appreciate a hand with a code reference.
800.133(A)(2) Communication wires and cables shall be separated at least 50 mm (2 in.) from conductors of any electric light, power, class 1, non-power limited fire alarm, or medium power network powered broadband communications circuits.
It's true that the word "penetration" is absent, and it's presence would have nullified your objection. However, if you had a room in commercial construction (say) and you ran Class 1 and 2 or 3 through those punch-outs in the aluminum stud for a hundred feet or so, I'd opine that you've violated the intent of the section, if not the wording.
It is standard practice here to keep the two separated whether required or not.
800.133 (A)(2)
This is repeated in 820.133 , 830.133 (840.133 refers to 770.133) , etc etc.....
~RJ~
For control wiring see art 725, for communications see art 800, most anything else is "power wiring".I am looking for the class "numbers" for the wires in the last post.