But 800.133 is for wires and cables attached to the outside of the building,
800.133 (A)(2) is for inside, separation for conductors not cables.
If you can accept that a cat 5 cable can run along side a RMC, then a cat 5 cable is allowed along side a NM cable. the NM and RMC are both chapter 3 wiring methods
I read this as repetitively addressing individual conductors vs. cables as well Tom.
In layman's terms that would be ok to run Cat 5 alongside NM , through the same hole(s) ,not ok in the same JB, troffer, etc
Do we agree?