low voltage in same hole

Status
Not open for further replies.

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
But 800.133 is for wires and cables attached to the outside of the building,
800.133 (A)(2) is for inside, separation for conductors not cables.
If you can accept that a cat 5 cable can run along side a RMC, then a cat 5 cable is allowed along side a NM cable. the NM and RMC are both chapter 3 wiring methods




I read this as repetitively addressing individual conductors vs. cables as well Tom.

In layman's terms that would be ok to run Cat 5 alongside NM , through the same hole(s) ,not ok in the same JB, troffer, etc

Do we agree?

~CS~
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I read this as repetitively addressing individual conductors vs. cables as well Tom.

In layman's terms that would be ok to run Cat 5 alongside NM , through the same hole(s) ,not ok in the same JB, troffer, etc

Do we agree?

~CS~

Yes, cables and conductors through a single hole are not the same thing. Two cables are permitted in one hole even if one of the cables is "low voltage".
 