low voltage lighting

Status
Not open for further replies.

koby

Member
I am installing a light fixture that has 2 - 200 watt 120 volt to 12 volt magnetic transformers that feed 20 - 10 watt quartz lamps. the 2 secondaries of the transformers are tied in paralel like the manufacturer is making 1 - 400 watt tranformer. When the power was turned on 1 transformer smoked. My experience with transformers tells me that the 2 secondaries cannot be tied together, am I correct? I realize I only need 1 200 watt transformer for this job but the the manufacturer has noted there is a 20 watt max. on lamp size.
 
iwire said:
Transformers secondaries can be tied together.

They will have to be 'in phase' with each other.

Can be, or should be? If they are connected in-phase and some unsuspecting person disconnects one of the primaries, they now have a 120v back-fed hot transformer in their hands.

Yeah, yeah, I know -- Turn Stuff Off First, but it still strikes me as an accident waiting to happen.

(And of course, if they are no connected in phase then one of them is likely to get smoked ...)
 
Holy lost souls Batman...look who came back. :grin:

tallgirl said:
Can be, or should be?

It sounded to me like factory wiring and they can pretty much do what they want.

My own choice would be no.
 
iwire said:
Holy lost souls Batman...look who came back. :grin:



It sounded to me like factory wiring and they can pretty much do what they want.

My own choice would be no.


Or it was connected by someone else and brought back as a defect. All the LV lighting trany's I have seen give 300 watt max on each terminal. You can get 300, 600 or 900 watt tranys with respectively, 1, 2, 3 sets of terminal screws.

I wonder if was meant to be wired like that or a screw up along the way somewhere


WB Tallgirl
 
Dennis Alwon said:
Or it was connected by someone else and brought back as a defect.

What I was saying is that it was not the OP that decided to parallel the transformers but the factory.

Obviously there was a defect....smoke came out.:grin:


All the LV lighting trany's I have seen give 300 watt max on each terminal.

That is the maximum the NEC allows per LV circuit. But a manufacturer is not bound by the NEC.
 
Why not divide the load into two groups and put half on each transformer?

Nice to have you back, Julie. :)
 