Low-voltage luminaire in bathtub zone

Status
Not open for further replies.

Chris K.

New member
Does the NEC permit installing a low-voltage (12V) luminaire above the tub (within the restricted zone)?

I know 410.4(D) prohibits pendant lights, track lighting, hanging and cord-connected fixtures in the bathtub zone, but I can't find anything in the 2002 NEC that addresses the low-voltage question.

Apparently surface-mounted or recessed luminaires are okay in the bathtub zone. Do you think that this "surface-mount" fixture (Model 809 3-light pan) can truly be considered surface-mounted, with respect to 410.4(D)??
 
Re: Low-voltage luminaire in bathtub zone

Interesting ,not listed for a wet or damp location.Says nothing about GFCI Protection.It does protrude beyond the drywall.My guess INHO is not suitable.I searched their web site and under UL that one was not there.
 
Re: Low-voltage luminaire in bathtub zone

I don't think that the 12 volts v. 120 volts is the issue. This fixture isn't a track light, a pendant light or a hanging and cord connected fixture so IMO the restrictions for within the tub zone wouldn't apply. The only question that remains is the location type. Is this a damp or wet location? The luminaire would need to be suitable for that specific environment.
 