517.80 Patient Care Areas
Equivalent insulation and isolation to that required for the electrical distribution systems in patient care areas shall be provided for communications, signaling systems, data system circuits, fire alarm systems, and systems less than 120 volts, nominal.
Need help with this,
* electrical distribution, is this refering to branch circuit wiring or feeders (distribution)?
* Insulation, does this mean if I am installing a data line in a patiant care area the insulation of the cat-5 cable would need to be rated for 90 degrees, same as the thhn I installed for power distribution?
* Isolation, the same cat-5 cable would need to be in an armored jacket or installed in conduit?
Clarification on this would be much appreciated.
Thanks!