chevyx92
Senior Member
- Location
- VA BCH, VA
Are you allowed to run "THHN" for low voltage wiring?
chevyx92 said:Are you allowed to run "THHN" for low voltage wiring?
steved said:At some point in time the low-voltage portions of article 551 were removed from the NEC. Article 551 of the 1996 NEC covered low-voltage wiring, but article 551 of the 2005 NEC does not. I don't have a '99 or '02 codebook, so I'm not sure when the change took place. The RVIA standard seems to be similar to what used to be in the NEC; in fact some of it is copied word-for-word.
ryan_618 said:Are you looking n the 2005?
jes25 said:ryan_618 said:Are you looking n the 2005?
No. We are on '02 here. I take it the '05 has an exception for class 2 wiring