Re: Low Voltave wire in wall space
Almost all Door bell and thermostat power supply's are class2 listed and 725.61(E) clearly allows CL2 and CL3 installed in dwellings. And 725.61(G) further allows many substitutions for Class 2 and Class 3 cables and is listed in Table 725.61.
400.8 does not allow any other flexible cables installed in, through, or behind building surface.
411.4 as Pierre has pointed out. But this section is for the installation low voltage lighting cable.
So door bell and thermostat wiring that is listed in table 725.61 is allowed to be "in the walls"