- Location
- New Jersey
- Occupation
- Journeyman Electrician
Had an interesting day at work today. Seems that our 4000 amp, 208Y/120 volt temporary service has a POCO voltage that's a little high. We're using a 208-480Y/277 transformer (which has no taps) to get the 480 volts that the elevators require. At the elevator controller we have 511 volts, which occasionally faults the drive for over-voltage. It was decided (not by us) to add a 3Ø, 100kw load bank at the controller location to create a voltage drop so the elevators would see around 480 volts. Anyone care to guess how that went?