For LPG fuel dispensers, Class I, Division 1 is the:
1. entire space within the dispenser enclosure [and]
2. 18 in. from the exterior surface of the dispenser enclosure to an elevation of 4 ft. above the base of the dispenser [and]
3. the entire pit or open space beneath the dispenser and within 20 ft. horizontally from any edge of the dispenser when the pit or trench is not mechanically ventilated.
Class I, Division 2 is [from grade] up to 18 in. aboveground and within 20 ft. horizontally from any edge of the dispenser enclosure, including pits or trenches within this area when provided with adequate mechanical ventilation