factoryrat
- Detroit
I’m working in a Class II Div I area. We ran RMC to 24 explosion proof “T” boxes and out of each box ran a short length of LFMC to a sensor. We used type “LT” liquidtight. We ran a ground wire from the electrical panel in the RMC and landed it to the ground screw in each box and ran a ground wire through LFMC to each sensor and landed it to ground screw in sensor. In other words everything is tied to our ground wire. We are now told we have to replace all 24, 2’ to 3’ lengths, of LT LFMC’s with type “LA” type LFMC. The reason we were given was the type “LT” liquidtight was not a proper ground and therefore not approved for this Classification of area. I think the “LT” LFMC was code compliant – what to you think? I was told the “LA” LFMC has a copper wire in it (which I can see) that makes it an acceptable ground. Have you ever heard of this as a reason for running type LA sealtight in this situation?
350.10 (2) Uses Permitted tells me to look at 502.4 (A) (e) which I did and therefore I believe “LT” LFMC is allowed to be used in Class II Div I locations. I hope some of you can tell me if I’m right or wrong.