mltech
Senior Member
- Location
- Ft. Lauderdale
That's how I see it!
That's how I see it!
Thanks for all the input.
Jim, this is exactly how I percieved it. Nothing says I can't do it.
We have installed loading dock lights that come with a yellow type SO cord with no plug and have installed them directly into a 1900 j-box. I was following the same installation procedures. Flexible cord with romex type connector into the fixture and then same set up into the supply box. All circuits are pigtailed so removing a fixture would not open the circuit. Of Course we would not work it live anyway.
I will see what kind of stance I can put up against the inspector. And will let you know.
Thanks again.
Mike
That's how I see it!
Jim W in Tampa said:"410.30(C) Electric-Discharge Luminaires (Fixtures).
(1) Cord Connected Installation. A listed luminaire (fixture) or a listed assembly shall be permitted to be cord connected if the following conditions apply: "
They key word here is SHALL BE PERMITTED.It is simply permitted.Nothing says its not permitted to connect the cord directly to the box.Use a strain relief cap with 1/2 threads and a locknut.
Thanks for all the input.
Jim, this is exactly how I percieved it. Nothing says I can't do it.
We have installed loading dock lights that come with a yellow type SO cord with no plug and have installed them directly into a 1900 j-box. I was following the same installation procedures. Flexible cord with romex type connector into the fixture and then same set up into the supply box. All circuits are pigtailed so removing a fixture would not open the circuit. Of Course we would not work it live anyway.
I will see what kind of stance I can put up against the inspector. And will let you know.
Thanks again.
Mike