Luminaires required to be grounded?

Status
Not open for further replies.

gregoryfast

Member
Location
Alaska
I am hoping I can get some help. I have always understood 250.110(1) to apply to luminaires. That if the fixed equipment is higher than 8' from the ground, it doesn't need to be grounded. I am working on an OSHA citation which is taken from the 1981 code that is essentially the same as 2002 code.

It seems that 250.112(J) requires the luminaire to be grounded regardless of height.

What is your take?

Thanks,

Gregory
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: Luminaires required to be grounded?

My take is that 250.112 overrides 250.110, in that it talks about specific types of equipment. In its turn, 250.112(J) refers you to Pat V of 410. Within Part V, 410.20 says we must ground the luminaries, and does not talk about height. I think the issue raised by the OSHA citation is valid.
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Luminaires required to be grounded?

I agree.

Plus, one would have a hard time finding a install that didn't meet one of the eight conditions in "shall be grounded under any of the following conditions:" of 250.110 !
 