- Tennessee NEC:2017
- Semi-Retired Electrician
For those that don't know, Lutron makes wireless switches that uses a master switch that you put in place of a regular SP or 3-way switch. Then they use a wireless remote switch called a Pico. Caseta is the most common model of this wireless set-up.
There is a way to use this in an existing 3-way circuit and keep one of the 3 way mechanical switches and use the Pico as an extra switch, effectively making this a 4-way circuit.
To use this setup, you replace one of the 3-ways (doesn't matter which one) with the master, or controller, switch. The master has 4 wires, black, red, blue, and white, also ground. You take the black from the master and tie it to the line/load wire. Then you take 1 of the travelers and tie it to the blue wire. It's important to note which traveler you used for the blue wire. Then tie the red wire to the remaining traveler. You either pass the neutral through with the white if needed, or cap it off.
At the other 3-way, you remove the common (line/load) and remember or tag it. Then the traveler that you tied to the blue wire remains on the switch. You remove the other traveler, tie it to the common, along with a jumper, and connect that back to the common terminal. This leaves one terminal empty. You then can add the Pico remote wherever its needed.
A customer has a 4-way circuit and would like to add another switch. I plan on using the method I described above and leave the 4-way switch, then add the Pico as the new switch. Does anyone see a problem with the 4-way being used along with this method?
I don't see a problem but wanted other "eyes" on it to check myself.