LV switchgear or AC Distrib Panel for welding receptacles - safety hazard?

Status
Not open for further replies.

irfan2222

Member
Question: Can AC Distribution Panel be used instead of LV MCC (LV switchgear) to supply to welding receptacles? is there a safety hazard if AC Distribution panel is used?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
There is no reason you can't use a distribution panel to supply welding receptacles, presuming of course that the equipment ratings are appropriate for the intended load. Welders are not motors, so I can't imagine supplying them from a motor control center. And you certainly don't need to use switchgear construction for this type of load. Are you being told otherwise? If so, by whom, and in what context?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
About the only issue I know of with welding loads involves the 'plug-on' jaw connection of breakers to aluminum bussing. Very rare occurence except with older production style resistance welders as found in 'automotive' factories.
 