Just want to confirm that what i have gleaned from the web is correct. Have existing system with M250 micros and envoy S. Adding some IQ8's. My understanding is i need a second gateway correct?

Another question: once this is set up, will it look just like a single system in the customer app? Anything else I should know?

Thanks
 
Just want to confirm that what i have gleaned from the web is correct. Have existing system with M250 micros and envoy S. Adding some IQ8's. My understanding is i need a second gateway correct?
Correct. M-series communicate with the Gateway L-N and IQ series communicate L-L (because there is no neutral) so there's a physical incompatibility and each needs their own compatible one.

Another question: once this is set up, will it look just like a single system in the customer app?

Only if you add the new Gateway to the existing system. Important not to create an new activation. These days you go into ITK and change the device count on the existing system. But yes, if you do it that way it looks like one system to the user.
 
Correct. M-series communicate with the Gateway L-N and IQ series communicate L-L (because there is no neutral) so there's a physical incompatibility and each needs their own compatible one.



Only if you add the new Gateway to the existing system. Important not to create an new activation. These days you go into ITK and change the device count on the existing system. But yes, if you do it that way it looks like one system to the user.
Thanks. But an IQ gateway seems to be backwards compatible With M and IQ micros, so one of those cant do a system with both? Or is it just not recommended? I see language like "should not" instead of "cannot"🤔
 
Thanks. But an IQ gateway seems to be backwards compatible With M and IQ micros, so one of those cant do a system with both? Or is it just not recommended? I see language like "should not" instead of "cannot"🤔
See this post. Sounds like the PLC connection on IQ Gateway is only to L1 and L2, so it can not talk to M series microinverters doing PLC on L and N.


Cheers, Wayne
 
See this post. Sounds like the PLC connection on IQ Gateway is only to L1 and L2, so it can not talk to M series microinverters doing PLC on L and N.


Cheers, Wayne
Ok, i must be losing my mind. A few hours ago i looked up the specs of an IQ gateway amd i could have sworn that under "comparability". It said IQ, M and S micros. So thata why i was confused. Not sure what i was looking at the first time, but thats clearly not correct.
 