Yes, it was brought up years ago.
However, most townships/cities/municipalities are a couple years behind on adopting new code. So now that most places have adopted 2008 NEC, it is now a NOTICEABLE problem. If you were still on the 2005 cycle, then it wasn't usually an issue because very few bedrooms required dimming greater than 1000w. Since AFCI protection now (2008 NEC...and 2011) includes living/dining rooms, this will be a common issue.
Tottaly understandable due to the fact that we adopt the code late. I only joined MH in 2007. However I have done much research on this site and there is not much devoted discussion. Until this tread and there have been many a troubleshooting AFCI ones in the past. This is the first reference to the 1000w dimmed load issue.
I found another thread that was closed way before the issue was debated.
http://forums.mikeholt.com/showthread.php?t=58727&highlight=AFCI+100+watt+dimming++max
I think that was wrong a posters question went unanswered.
Close a thread because it is going in the wrong direction, but not because of being stale or not interesting to the Moderator.