This can be fairly easily achieved by phase configuration. For example, using 800 kV spacing, 2000 amps (1000 per side), and rolling fromYes, completely sure. We need to achieve 0.4 uT (microTesla) at 50m from the center of the line.
A-A
B-B
C-C
to
A-C
B-B
C-A
gets me around an 85% magnetic field reduction at 50m (0.643 uT went to 0.098 uT).
Putting in a return ground made the field less under the line but slightly higher at the 50m point (0.861 vs. 0.643 uT unrolled and 0.115 vs. 0.098 uT rolled).
It is also interesting to look at what happens when one side of the structure feeds power in a different direction from the other side (say for a loop feed in and out of a substation).