Again thanks a lot to all of you. All of you are very helpful.
Here's what I come up with for load calculation. This is just APPROXIMATE because I still don't know the kW of the appliances that will be installed. But mainly I would like to know if my load calculation procedure is correct. I will adjust the calculated numbers later.
4200 sq ft Single Dwelling
Computed load
General lighting load
4200sq ft at 3va /sq ft = 4200 x 3 = 12,600
Small Appliances load:
Dishwasher 1500
Garb disp 1500 3000
Laundry 1500 1500
________
Total general light & appliances load 17,100
3000 v-a at 100% load 3,000
17100-3000 = 14,100 v-a at 35% 4,935
_________
Net General Lighting and small appliances load 7,935
Range Load 8,000
Dryer load 5,500
Hot tub load 8,000
Water heater 2,500
Wall Mounted oven/microwave 3,000
Air conditioning 10,080
__________
Total Load 45015
For 120/240-volt 3 -wire single phase service feeder
45015 /240 volts = 187.6 A