Now that I have your attention..
I have a service call in a condo built in the 1960s. The service has a fused disconnect downstairs. I cannot find a main bonding jumper in it. There is a 208/120V 3 wire system up to the unit- L1,L2,N. Feeders terminate in a main breaker at unit. MBJ is connected at the panel. No original riser prints available. I cannot access any other unit to see if the replaced panel is a change from original design. My question is: If the EMT is the ground and I am looking at a "3 wire with ground" I would need to remove the bonding jumper in panel and isolate neutral block. Then I would need to add the MBJ at the first disconnect. My concern is that this is a change from the original design. Additionally, I do not like to use EMT as the sole ground conductor. But, Clearly, leaving it as it is keeps a parallel circuit in place for the neutral (unbalance) current. In other services, I have seen circuit breakers used as connection blocks in metering equipment. The AHJ and I agreed this was solely as a "terminal" to connect the feeders to the meter equipment stabs and that the main disconnect was at the panel in the units. The difference in those cases was that the conduit carring L1,L2,N was PVC. I can see no such purpose for the fuses in enclosures as the breakers were used. Any Ideas as to why to go one way or the other? Was there a time when the MBJ could be at a location not in the individual disconnect and I am just missing it? (NOT an assembly per 250.24(5)(B) exception 1, they are individual disconnects)