Those grounding requirements are for a service-supplied mobile home or manufactured home. There is no service.
As such, grounding requirements fall back to Article 250. 550.32(B)(5) even hints to this where it says "The instructions shall clearly state that other methods of grounding are found in Article 250."
250. 550.32(B)(5) even hints to this where it says "The instructions shall clearly state that other methods of grounding are found in Article 250."
IMO the above quoted simply says the manufacture in their instructions for example below will specify one method i.e. ground rods but other methods i.e. a plate electrode are found in article 250.
" Use a listed 5/8 inch diameter by eight foot long iron electrode or nonferrous
rod of at least 1/2 inch diameter by eight feet long for grounding (larger sizes
may be required by the LAHJ due to soil impedance).
Drive the electrode to a depth of not less than eight feet so that at least eight
feet of the electrode is in contact with the soil.
When rock is encountered, the electrode may be driven at an angle not to exceed
45 degrees from vertical or buried in a trench that is at least 2-1/2 feet deep."
Those grounding requirements are for a service-supplied mobile home or manufactured home. There is no service.
As such, grounding requirements fall back to Article 250.
IMO the requirements specify feeder supplied manufactured homes as well as service supplied manufactured homes. The manufacture IMO doesn't care if the supply is a generator or a utility