Re: Main Bonding Jumper
When there is no equipment ground wires, and the branch circuits are in metal conduit, both buses are neutral/ground buses.
The screw is the main bonding jumper.
The bond strap, link, or jumper is part of the neutral/ground circuit. Ground fault current will flow, on the link, when the screw is in the left bus to the enclosure. It will not flow when in the other side.
The point is the link has different functions according to the equipment ground terminations.
[ May 08, 2003, 02:05 PM: Message edited by: bennie ]
When there is no equipment ground wires, and the branch circuits are in metal conduit, both buses are neutral/ground buses.
The screw is the main bonding jumper.
The bond strap, link, or jumper is part of the neutral/ground circuit. Ground fault current will flow, on the link, when the screw is in the left bus to the enclosure. It will not flow when in the other side.
The point is the link has different functions according to the equipment ground terminations.