Just installed a new 400a. 240v. 4 wire red leg delta service consisting of 2-200a. 3ph meters & MBs, all mounted on the building exterior.
As one tenant only required single phase for an existing 100a. panel I ran a 3 wire, single phase, 100a. 120/240 feeder from the main breaker load side, about 30' along the exterior wall surface to a 100 amp disconnect mounted immediately upon entry.
Conduit is 1" emt, all fitting are raintite, wire is #3 thhn.
I got a violation for this, without explanation, other than the #3s weren't properly protected on the 200a. MB.
Does the tap rule not apply here? I cited 240.21(b)(5) to the inspector to no avail.
He did seem confused though and said he would investigate further.
Any comments?
Much obliged.