S SHILGEFORT Member Mar 25, 2008 #1 Is a main breaker required in the panel located in a farm house if the feed has overcurrent protection an outside location on the srvice pole?
Is a main breaker required in the panel located in a farm house if the feed has overcurrent protection an outside location on the srvice pole?
iwire Moderator Staff member Location Massachusetts Mar 25, 2008 #2 SHILGEFORT said: Is a main breaker required in the panel located in a farm house if the feed has overcurrent protection an outside location on the service pole? Click to expand... So you have overcurrent protection at the pole, then a feeder to the farm house? If so 225.31 applies and you need a disconnecting means at the farm house. 225.32 for location. 225.36 requires it to be service rated 225.37 requires identification 225.39 for the minimum rating.
SHILGEFORT said: Is a main breaker required in the panel located in a farm house if the feed has overcurrent protection an outside location on the service pole? Click to expand... So you have overcurrent protection at the pole, then a feeder to the farm house? If so 225.31 applies and you need a disconnecting means at the farm house. 225.32 for location. 225.36 requires it to be service rated 225.37 requires identification 225.39 for the minimum rating.
radiopet Senior Member Location Spotsylvania, VA Mar 25, 2008 #3 Yep....and don't forget it would require it's own GES as well at this "Structure"