main breaker required?

Status
Not open for further replies.
Is a main breaker required in the panel located in a farm house if the feed has overcurrent protection an outside location on the srvice pole?
 
SHILGEFORT said:
Is a main breaker required in the panel located in a farm house if the feed has overcurrent protection an outside location on the service pole?

So you have overcurrent protection at the pole, then a feeder to the farm house?

If so 225.31 applies and you need a disconnecting means at the farm house.

225.32 for location.

225.36 requires it to be service rated

225.37 requires identification

225.39 for the minimum rating.
 