Main breaker trip

Status
Not open for further replies.

Todd0x1

Senior Member
Location
CA
One circuit was just laying on the floor, and I wanted to find out what was on it. I dead-shorted it (in such a way that it didn't arc), and it tripped a single pole 20 amp breaker in a subpanel as well as the 100 amp breaker which feeds that subpanel.
That's a good way to start a fire. Please buy yourself one of these, there's an accessory kit that gets you alligator clip leads
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
That's a good way to start a fire. Please buy yourself one of these, there's an accessory kit that gets you alligator clip leads
There isn't any way a soft trip will start a fire.
I have one of those circuit finders, though. Hard to plug it in to the end of a bare romex. I don't have alligator clips
 

Todd0x1

Senior Member
Location
CA
There isn't any way a soft trip will start a fire.

It can happen. Bad connection between the breaker and you, the wires stick together when you touch them, circuit impedance such that current is limited below instant trip range so breaker doesn't trip right away. Had it happen unintentionally once where a wire welded itself to a box. Took many seconds for breaker to trip, thing was glowing.
 
Status
Not open for further replies.
Top