Yes. The two devices were never selectively coordinated. If the upstream device has an adjustable trip unit, which has been common for the past 20 years, it was shipped from the factory set to the minimum.
 
It is also very possible that the main has ground fault protection but the feeder and branch breakers do not.

IMHO you should not be adjusting the breaker pickup without understanding the implications for arc flash hazard at the facility in question.

-Jon
 
Am I able to possibly fix the issue by adjusting the breaker's Short-time Pickup?


Sent from my iPhone using Tapatalk
Can't really answer without seeing the breakers' Time Current Curves for both overcurrent and ground faults.
Do you have any idea how much current was flowing when the trip occurred?
 
Because of liability, I usually suggest to the customer to get an engineered coordination study, to get the proper settings on a ground fault breaker before making any changes. As others have said, they usually are set to the minimum settings from the factory, and rarely get changed until they start having problems.
 