iwire said:That was not really what I was getting at, some of the posters where focusing on the breaker tripping because of inrush currents and seem to have missed the fact it was tripping more times when the utility failed.![]()
Arce2ee said:How do you know if undervoltage relays are causing the problem? Would I have to have the breaker manufacturer send a field rep to perform a diagnostic or is there a simpler way?
Arce2ee said:You are correct that it only trips on loss of utility. Under normal operation the load on the building is no where near high enough to trip the breakers even with inrush currents.
What you need here is Super ZOG to pull up in his million dollar rig and acess the situation,,,,,,,,,this gonna be be pretty pricey Im sure.....zog said:First of all, I dont know anything, you havent provided enough information about the system at all, many assumptions are being made here.
Second, there is no "problem" the UV relays are doing just what they are supposed to do on a loss of utility power, they are also protecting your equipment from overloads. Now the settings may not be correct, when was the last time you had a coordination study performed?
Third, if you are going to call a field rep, call someone certified and from an independent 3rd party, but you dont need to call anyone yet because you dont even know IF you have a problem yet.
Get some info, name plate data from the breaker, any relays on the switchgear, what are the main breakers tripping on? Take some pictures of the breaker, trip unit, and overall of the switchgear and post them here.
How do you know if undervoltage relays are causing the problem? Would I have to have the breaker manufacturer send a field rep to perform a diagnostic or is there a simpler way?
POWER_PIG said:What you need here is Super ZOG to pull up in his million dollar rig and acess the situation,,,,,,,,,this gonna be be pretty pricey Im sure.....Oh yeah, and don't be alarmed when he finally makes it out of the truck, with full bore linear super dooper PPE on of course, looking like one of the ghost busters.....lol.....just kidding..........kinda:roll:
zog said:The REAL question here is, WHY do you lose power from the utility so often?
Arce2ee said:So far the worst power reliablity I have ever run into. Local residents told our owner representatives that it is not unusal to be walking through the local superstore and the power to drop out.
In one instance the breakers were reset before the utility was restored and they tripped again when the utility was restored. What could be causing these to trip?