Imagine there is a certain situation in a residential installation; where the panel was not sufficiently bonded to earth ground, however the home was nearly completely wired. While pulling in a 14-2 Romex, ground touched busbar, and touched panel enclosure.
The circuits which already had their grounding conductor connected to the grounding busbar within the panel, had their grounding conductor red hot, as was the grounding conductor that touched busbar and panel. This caused some damage.
The question is why wouldn't the main breaker trip? Breakers are designed to trip where there is excessive current, and it seems to me this would be excessive current.. is it possible that there was enough resistance to keep the current under 200A? Also, if this system had sufficient bonding to earth ground, would it have tripped the breaker?
The circuits which already had their grounding conductor connected to the grounding busbar within the panel, had their grounding conductor red hot, as was the grounding conductor that touched busbar and panel. This caused some damage.
The question is why wouldn't the main breaker trip? Breakers are designed to trip where there is excessive current, and it seems to me this would be excessive current.. is it possible that there was enough resistance to keep the current under 200A? Also, if this system had sufficient bonding to earth ground, would it have tripped the breaker?