Main breaker won't turn on

Status
Not open for further replies.
Good chance it's time for a panel update.
Why? A Murray, not zinsco or similar, so why? Unless of course bad corrosion from some type damage or exposure. Are some of the older Murray defective??

Own home has QO panels that are 50 years old. No corrosion. Even on the 4/0 and 2AWG aluminum cables after about 20 years when torques checked no further tightening. Have never needed to replace a QO breaker.

Every 10 years or so have a heavy duty plug with a 30A breaker, plug in, throw breaker, verify the 20A QO's trip, never a failure.
 
Why? A Murray, not zinsco or similar, so why? Unless of course bad corrosion from some type damage or exposure. Are some of the older Murray defective??

Own home has QO panels that are 50 years old. No corrosion. Even on the 4/0 and 2AWG aluminum cables after about 20 years when torques checked no further tightening. Have never needed to replace a QO breaker.

Every 10 years or so have a heavy duty plug with a 30A breaker, plug in, throw breaker, verify the 20A QO's trip, never a failure.
I haven't seen Murray for years and I honestly thought they were discontinued.
 
Well James answered that. But you, being inexperienced with this, probably shouldn't attempt it. I was just saying what I had to do to get power back on in an emergency. Maybe your journeyman can help you with this.
Messing with un fused hot wires should be done by someone who understands the meaning of dead short or fault for sure.
 
Yes but they sold separate lines for quiet a while the old Murray mains are not Siemens mains though. The breakers are mostly interchangeable with exception to the older Murray that has an extra notch in it.
I saw Murray occasionally but was not real up on it. Can you still buy a Murray main?
 
Why? A Murray, not zinsco or similar, so why? Unless of course bad corrosion from some type damage or exposure. Are some of the older Murray defective??

Own home has QO panels that are 50 years old. No corrosion. Even on the 4/0 and 2AWG aluminum cables after about 20 years when torques checked no further tightening. Have never needed to replace a QO breaker.

Every 10 years or so have a heavy duty plug with a 30A breaker, plug in, throw breaker, verify the 20A QO's trip, never a failure.
IMHO, QO was the best breaker out there, still is best I know. Seeing some issues with I LIne, which is a shame. .
 
IMHO, QO was the best breaker out there, still is best I know. Seeing some issues with I LIne, which is a shame. .
Best is siemens in my opinion. They have mains that work and I hate QO loose bussing along with CH for the same reason. QO and CH afci are giant and GE and Eaton mains seam to be the ones that either fail in the on or off position. QO load centers also had poorly designed ground bars but so did everyone else at the time.
 
Can you back feed any breaker?

I've done a lot of them, but I can't say any. Generally a backed breaker also requires a means to secure it in place. It could be a screw or some other locking means that the mfg can supply.
If a loadcenter was built before the hold down requirements were added there is not much of chance of finding a hold down to comply.
 
Best is siemens in my opinion. They have mains that work and I hate QO loose bussing along with CH for the same reason. QO and CH afci are giant and GE and Eaton mains seam to be the ones that either fail in the on or off position. QO load centers also had poorly designed ground bars but so did everyone else at the time.
I did like Siemens for awhile but turned against them. Dealer wanted $400 for a metal switchgear plate with breaker KO. Where I now work, large Siemens breakers give out far more often than Square D.
Reading up on Siemens’ history didn’t help either.
 
You find any place in the panel to put a 100 amp breaker. Remove the power wires from the original main breaker and connect them to the new 100 amp you added.

You'd probably have to splice/add to the cable, and working it hot
You would also have to bolt the backfed breaker into the panel.
 
You would also have to bolt the backfed breaker into the panel.
If it's permanent, yes. But that was in reference to what Little Bill was talking about, a temporary fix until the original main could be replaced.

I added a comment about fastening in place on a later question asking if we can backfeed any breaker
 
... Breakers should be exercised every so often to keep things working. Most of us never do it. Even those of us that know we should.
Yep. The cobbler's children go barefoot...
Heck, I took the cover off of my panel 10 years ago to change a breaker, hadn't put it back on again until last year when I added solar.
 
Being a Murray, it’s probably pretty old, and the grease on the mechanism has dried out. If none of the other suggestions work, that’s probably what it is. The contacts are spring loaded, and they are not moving far enough to latch. Sometimes repeated movements of the handle can loosen it up, but it’s best to just replace.

Sometime the ole Fonzy trick works when these breakers don’t want to re-latch.
Just smack the breaker with the butt of your screwdriver a couple times has worked for me.
 