Jakewhis said:
when are you allowed to use a main lug panel board and where is this in the code book.

When the feeder supplying the panel is protected by overcurrent matching or below the panels rating.

408.36
 
Look at 230.71. The Main Breaker is usually present to serve as a disconnect for the service. If there is a disconnect ahead of the panel (it is installed as a subpanel) and the disconnect provides overcurrent protection for the feeder, then you may use a Main Lug panel. Usually (and this is an oversimplification) Main Lug panels may only be used as sub-panels.
 
haskindm said:
Look at 230.71. The Main Breaker is usually present to serve as a disconnect for the service. If there is a disconnect ahead of the panel (it is installed as a subpanel) and the disconnect provides overcurrent protection for the feeder, then you may use a Main Lug panel. Usually (and this is an oversimplification) Main Lug panels may only be used as sub-panels.
So say you have a shop that you are going to feed with a 100 amp breaker from the house, the sub panel at the shop can be a 100amp main lug panel.
 
Jakewhis said:
So say you have a shop that you are going to feed with a 100 amp breaker from the house, the sub panel at the shop can be a 100amp main lug panel.


A sub-panel in a separate structure would require a disconnecting means. Typically a main CB is the simplest way to accomplish this.
 
I am not sure of prices in your area but here in ohio 100 amp 20 space main lug sub panel is around $45.00, the 100 amp 20 space main breaker value pack with 5 20 amp breakers is $59.00 I just buy the value pack you will need breakers anyway.
 