Good day all,
Please excuse this post if this has already been addressed and, if so, could someone provide a link to the thread addressing it.
I recently installed a subpanel to service an addition to my house. When I try to energize the subpanel the main breaker trips. There are no loads presently on the subpanel as the branch circuits haven't been terminated yet so it is essentially just the feeder connected to the busses. I checked for shorts at the subpanel lugs and, when checking for continuity between the lines and ground, I had a short between my black and ground. I pulled the breaker feeding the subpanel, checked continuity between black and ground, and showed a short as to be expected. I did loosen the connection on the cable connector at the subpanel and then loss tone when checking for continuity and have never been able to get a continuity tone since.
However, I have tried several different things and the results are still the same; the main CB trips immediately:
Turned off all remaining breakers in the main panel so that the only possible draw in the subpanel, which has no loads currently on it.
Connected the feeder to a different breaker.
I could be wrong but I think that I have a short in the feeder cable and that cable will have to be replaced but I am more concerned about why the main trips before the branch breaker does.
Thank you in advance for any advice.
Please excuse this post if this has already been addressed and, if so, could someone provide a link to the thread addressing it.
I recently installed a subpanel to service an addition to my house. When I try to energize the subpanel the main breaker trips. There are no loads presently on the subpanel as the branch circuits haven't been terminated yet so it is essentially just the feeder connected to the busses. I checked for shorts at the subpanel lugs and, when checking for continuity between the lines and ground, I had a short between my black and ground. I pulled the breaker feeding the subpanel, checked continuity between black and ground, and showed a short as to be expected. I did loosen the connection on the cable connector at the subpanel and then loss tone when checking for continuity and have never been able to get a continuity tone since.
However, I have tried several different things and the results are still the same; the main CB trips immediately:
Turned off all remaining breakers in the main panel so that the only possible draw in the subpanel, which has no loads currently on it.
Connected the feeder to a different breaker.
I could be wrong but I think that I have a short in the feeder cable and that cable will have to be replaced but I am more concerned about why the main trips before the branch breaker does.
Thank you in advance for any advice.