House electrical just upgraded from 100a to 200a. A new garage was built as well and the new riser, 200a meter box with a main 200a disconnect box directly below it was installed there because it was closer to the utility pole than the house. The feeders from the main disconnect to the house were buried in Sch80 and the new 200a main house panel was wired as a subpanel, which also has (2) 60 amp sub panels feeds, one to the garage and one to a small storage/work shed.
The garage is theoretically attached to the house by a roof and walkway but to me nevertheless represents a detached garage and separate building. The service feeders enter the main house subpanel direct to the lugs without a main breaker or non-fuse disconnect. Neither of the 60 amp subpanels have a main breaker or disconnect because they both have 6 or less breakers to shut off all power, which I believe is allowable in lieu of a single main breaker.
My question is doesn't the main house subpanel require a 200 amp main breaker as well at its nearest point where the feeders enter the home structure? The main disconnect just below the meter on the garage building was naturally installed to meet code where the service feeders enter the garage building but it doesn't seem to satisfy the code for the main house subpanel. Distance from main disconnect to house panel is only 20 feet but I don't think distance matters at all but rather the fact that the other end of the service feeders are entering a building to a panel with far greater than 6 breaker disconnects.
Am I right or wrong that a main 200a breaker is missing from the point where the feeders enter the house panel?
The garage is theoretically attached to the house by a roof and walkway but to me nevertheless represents a detached garage and separate building. The service feeders enter the main house subpanel direct to the lugs without a main breaker or non-fuse disconnect. Neither of the 60 amp subpanels have a main breaker or disconnect because they both have 6 or less breakers to shut off all power, which I believe is allowable in lieu of a single main breaker.
My question is doesn't the main house subpanel require a 200 amp main breaker as well at its nearest point where the feeders enter the home structure? The main disconnect just below the meter on the garage building was naturally installed to meet code where the service feeders enter the garage building but it doesn't seem to satisfy the code for the main house subpanel. Distance from main disconnect to house panel is only 20 feet but I don't think distance matters at all but rather the fact that the other end of the service feeders are entering a building to a panel with far greater than 6 breaker disconnects.
Am I right or wrong that a main 200a breaker is missing from the point where the feeders enter the house panel?