Main disconnect on building for 2020?

JoeNorm

Senior Member
I was talking to an inspector from my area yesterday and he mentioned there may be a new requirement to have a main service disco on the residence(outside, on side of building) for 2020. Presumably for first response reasons but I don't know for sure. Anyone know more about this?
 

PaulMmn

Senior Member
Not a bad idea, as long as the breaker box is inside, out of the weather! Keep those AFCIs and GFCIs nice and dry.
 

Dennis Alwon

Moderator
Staff member
Not a bad idea, as long as the breaker box is inside, out of the weather! Keep those AFCIs and GFCIs nice and dry.
If the box was inside then there would be no reason for this section. It requires the diso outside.

230.85 Emergency Disconnects(s)
For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped. Each disconnect shall be one of the following:

(1) Service disconnect(s) marked as follows: EMERGENCY DISCONNECT, SERVICE DISCONNECT

(2) Meter disconnect(s) installed per 230.83(#) and marked as follows: EMERGENCY DISCONNECT, METER DISCONNECT, NOT SERVICE EQUIPMENT

(3) Other than listed disconnect switch(es) or circuit breaker(s) on the supply side of each service disconnect that are suitable for use as service equipment and marked : EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT

Markings shall comply with 110.21(B)
 

PaulMmn

Senior Member
If the box was inside then there would be no reason for this section. It requires the diso outside.
I'm talking about the box with all the branch breakers, not the main disconnect. Outside, you've got the meter, and one big switch to cut off all power to the building. That's it. Keep the branch breakers (in their box) inside where it's dry!
 

Dennis Alwon

Moderator
Staff member
I'm talking about the box with all the branch breakers, not the main disconnect. Outside, you've got the meter, and one big switch to cut off all power to the building. That's it. Keep the branch breakers (in their box) inside where it's dry!
Gotcha--- more money that way but I agree it is probably a better job
 

romex jockey

Senior Member
One local poco's recent policy is to install cutouts on the serving pole on my turf

If one thinks on it, most serious fires end up having the poco disco the service at the pole anyways

~RJ~
 

kwired

Electron manager
One local poco's recent policy is to install cutouts on the serving pole on my turf

If one thinks on it, most serious fires end up having the poco disco the service at the pole anyways

~RJ~
But with disconnect that is accessible to fire fighters, they don't have to wait for POCO to know the power is off.

Finding said disconnect is another story. Even if on outside, property owners may still hide it to certain extent.
 

Buck Parrish

Senior Member
So if I'm wiring a new home. They want the inside panel in the garage exactly behind the meter. Are you saying I'd have to install a disconnect right behind the panel? Is that before the meter or on the HO side?
That would be significant if you do a lot of 400 amp services.
 

kwired

Electron manager
So if I'm wiring a new home. They want the inside panel in the garage exactly behind the meter. Are you saying I'd have to install a disconnect right behind the panel? Is that before the meter or on the HO side?
That would be significant if you do a lot of 400 amp services.
Might as well plan to put service disconnect outside and maybe use main lug panel inside. Though it doesn't require the service disconnect to be outside, just an emergency disconnect to be outside.

See section content Dennis posted in post 4.

Note it does not say it has to be on the dwelling either just "installed in a readily accessible outdoor location." I see potential changes for clarification coming in the next code.
 

Dennis Alwon

Moderator
Staff member
So if I'm wiring a new home. They want the inside panel in the garage exactly behind the meter. Are you saying I'd have to install a disconnect right behind the panel? Is that before the meter or on the HO side?
That would be significant if you do a lot of 400 amp services.
Right now you don't have to worry but if NC accepts this section with no amendments then you will need either 1- 400 amp disconnect next to the meter or 2- 200 amp discos next to the meter before you go inside to the sub panels.

I am not sure what an emergency disconnect is considered if not part of the service equipment. A disconnect before the meter???
 

kwired

Electron manager
Right now you don't have to worry but if NC accepts this section with no amendments then you will need either 1- 400 amp disconnect next to the meter or 2- 200 amp discos next to the meter before you go inside to the sub panels.

I am not sure what an emergency disconnect is considered if not part of the service equipment. A disconnect before the meter???
That is why I see potential changes for clarification in next code. Too vague from what I am seeing and contradicting to previous existing requirements of art 230. Generally first switch needed to be the service disconnecting means, then they apparently now want this switch but as worded doesn't necessarily need to be the service disconnect.

Apparently a "meter disconnect switch" required by some POCO's (though many of those are not on a dwelling but rather on 200 amp and less 480 volt applications) would be allowed to be considered serving this purpose, and yet still require an additional service disconnect.
 

ron

Senior Member
It will be interesting if breakers installed outside in cold environments will experience higher trip values, and how the AHJ will relate it to downstream wire size protection.
 

jim dungar

Moderator
Staff member
It will be interesting if breakers installed outside in cold environments will experience higher trip values, and how the AHJ will relate it to downstream wire size protection.
In cold environments, thermal magnetic breakers will carry more current, is that what you are referring to? But for the most part the 'up North here' nobody takes the characteristics into consideration. There are thousands of multi-metering applications installed where no adjustments have been required.


The emergency disconnect, like the meter disconnect, probably would not need to be rated to close into a fault condition, and may not even need to break bolted fault conditions, unlike a service disconnecting means.
 

ron

Senior Member
In cold environments, thermal magnetic breakers will carry more current, is that what you are referring to? But for the most part the 'up North here' nobody takes the characteristics into consideration. There are thousands of multi-metering applications installed where no adjustments have been required.


The emergency disconnect, like the meter disconnect, probably would not need to be rated to close into a fault condition, and may not even need to break bolted fault conditions, unlike a service disconnecting means.
That is what I was thinking of.
I think most folks will use the emergency disconnect as the service disconnect whenever possible.
 

JoeNorm

Senior Member
In my area(rural area) all of our meters are placed by the transformers, wherever they may be. Usually somewhere along the main road. For the last 10 years or so our utility has required a main disconnect out there along with the meter for any major modification or new construction. I am guessing we are already satisfying the new requirement by doing it this way.
 

kwired

Electron manager
In my area(rural area) all of our meters are placed by the transformers, wherever they may be. Usually somewhere along the main road. For the last 10 years or so our utility has required a main disconnect out there along with the meter for any major modification or new construction. I am guessing we are already satisfying the new requirement by doing it this way.
Same thing with most rural services around here, particularly 400 amp and less single phase. Three phase usually 200 amp or less and sometimes 400 amps.

NEC is pretty vague on where this emergency disconnect must be located. I can see future changes possibly coming to tell us it needs to be on the building or maybe something like within 30 or 50 feet.
 

ggunn

PE (Electrical), NABCEP certified
Here in Austin the AHJ has had the requirement for an external service disconnect for many years. Under "you touch it, you fix it" we have to install one if it's not there any time we add a PV system to a residence, even if it lands on a backfed breaker in the MDP.
 

don_resqcapt19

Moderator
Staff member
In cold environments, thermal magnetic breakers will carry more current, is that what you are referring to? But for the most part the 'up North here' nobody takes the characteristics into consideration. There are thousands of multi-metering applications installed where no adjustments have been required.


The emergency disconnect, like the meter disconnect, probably would not need to be rated to close into a fault condition, and may not even need to break bolted fault conditions, unlike a service disconnecting means.
Why don't we take that into account? How is a breaker that trips 25% higher than nameplate for at least 5 months of the year, in my area, a code compliant installation?
 

jim dungar

Moderator
Staff member
Why don't we take that into account? How is a breaker that trips 25% higher than nameplate for at least 5 months of the year, in my area, a code compliant installation?
Based on the lack of any significant number of reported issues with this type of installation, I would guess the NEC tables for conductor sizing are sufficiently conservative and therefore the overcurrent protective device performance is satisfactory.

In my locale, the outdoor breaker are almost always, like 300 days/year, under 40°C . In fact, they may hardly often even exceed 25°C, for more than 3 hours at a time, unless they are are south facing.
 

ggunn

PE (Electrical), NABCEP certified
Why don't we take that into account? How is a breaker that trips 25% higher than nameplate for at least 5 months of the year, in my area, a code compliant installation?
Doesn't conductor ampacity also increase under those conditions?
 

don_resqcapt19

Moderator
Staff member
Doesn't conductor ampacity also increase under those conditions?
It code permitted increase is not as much as the increase in the trip point. The maximum multiplier in 310.15(B)(2)(a) is 1.15. Also, in many cases only a very small part of the conductor run is outside. Square D shows a 25% shift for their larger breakers in a 50°F ambient. While there would be some slight increase in the interior of the enclosure, I expect that in my area, a single main breaker in an exterior enclosure would operate at or below 50°F for about 5 months of the year.

The shift is even worse for some smaller breakers. It appears to me that a 25°C (77°F) can place the long term trip at 2x breaker rating.
 

Attachments

jim dungar

Moderator
Staff member
Don,

For derating purposes, you need to find the temperature derating curves and not simply shift the standard TCC. Use their publication called "Current Carrying Capacity In Special Applications" (0100DB0101).

At 0°C:
QOT 20A trips around 22A,
QO 20A trips around 26A
QOM100A trips around 125A
QOM 200 trips around 260A
 

don_resqcapt19

Moderator
Staff member
Don,

For derating purposes, you need to find the temperature derating curves and not simply shift the standard TCC. Use their publication called "Current Carrying Capacity In Special Applications" (0100DB0101).

At 0°C:
QOT 20A trips around 22A,
QO 20A trips around 26A
QOM100A trips around 125A
QOM 200 trips around 260A
Jim,
And that shows a 25% increase in the trip for the larger breakers. However the SquareD document that I have shows the 25% increase at 10°C, not zero. The document is titled "Determining Current Carrying Capacity in Special Applications", but has the same publication number. How is a 25% increase in the trip for 5/12s of the year code compliant? As far as their smaller breakers what does the dotted line to the right that is titled "maximum trip times at 25°C" mean. To me is says that the maximum trip time at that temperature is much higher than the breaker rating.
 

jim dungar

Moderator
Staff member
Don,

My copy of this publication is from July 1988 (#SD361 R1) and has the same curves as the link I provided.

The dashed lines on the trip curve should be based on the NEMA standard AB-2 for a single pole breaker, rather than on the actual breaker. This is probably a worse case 'long time delay', but honestly, I have never seen a clear explanation of when/how this reference would be used.
 

don_resqcapt19

Moderator
Staff member
Don,

My copy of this publication is from July 1988 (#SD361 R1) and has the same curves as the link I provided.

The dashed lines on the trip curve should be based on the NEMA standard AB-2 for a single pole breaker, rather than on the actual breaker. This is probably a worse case 'long time delay', but honestly, I have never seen a clear explanation of when/how this reference would be used.
Jim,
The document I am looking at for the larger breakers is "Determining Current Carrying Capacity in Special Applications Data Bulletin 0100DB0101"dated 06/01. That document also seems to say that you can't even use those breakers where the ambient temperature at the breaker would fall be low -10°C (14°F).
Square D circuit breakers can be applied in ambient temperatures within the range of -10°C to 60°C (14°F to 140°F). This document provides guidelines to follow when adjusting for ambient conditions.
UL has told me that this is a 110.3(B) instruction and prohibits the installation of the breaker in an outside location in my area.

As far as the dashed line, we just ignore it? How is the dashed line different from the 40°C trip band on the same trip curve?

I think that the temperature sensitiviy of thermal magnetic breakers is just something that has been ignored for a long time. Maybe there are no real issues with the trip change, but I can see cases where it could have an impact. If I worked for Leviton, I would be pushing this issue. They use "hydraulic" breakers that are not temperature sensitive. However that has a cost impact and is one of the reasons why their panels are more expensive.
 

jim dungar

Moderator
Staff member
How is the dashed line different from the 40°C trip band on the same trip curve?
The dashed line is not a characteristic of the breaker shown in the TCC. It is representative of a generic worst case device.

I can't think of any breaker that would not be somewhat affected by temperatures below 14°F. Many greased mechanism parts tend to be sluggish at 'negative' temperatures.
 

don_resqcapt19

Moderator
Staff member
The dashed line is not a characteristic of the breaker shown in the TCC. It is representative of a generic worst case device.

I can't think of any breaker that would not be somewhat affected by temperatures below 14°F. Many greased mechanism parts tend to be sluggish at 'negative' temperatures.
So we shouldn't use breakers outside where it gets cold. With the emergency disconnect rule, I think we will see a lot more outside service overcurrent protective devices. Maybe an Informational Note should be added to 230.85.
 

jim dungar

Moderator
Staff member
So we shouldn't use breakers outside where it gets cold.
I didn't say that.

Our industry has 50+ years of outdoor breaker installation history, particularly with multi-meter centers. I have no significant amount anecdotal evidence of outdoor breakers not offering appropriate protection except when they overheat in sunshine.
 

Coppersmith

Senior Member
I was talking to an inspector from my area yesterday and he mentioned there may be a new requirement to have a main service disco on the residence(outside, on side of building) for 2020. Presumably for first response reasons but I don't know for sure. Anyone know more about this?
If the circuit breaker panel is located outside and has a main breaker, can this main breaker serve as the above mentioned main service disco?
 

Coppersmith

Senior Member
The cold breaker problem being discussed could be solved by adding a heater to an outdoor panel. This is not a problem in my area however since it's still about 60F outside in January. We would have to opposite problem. A sun-heated outdoor panel may cause breakers to trip too soon. Dedicated breaker panel a/c systems are too expensive although venting indoor air into it may be possible.
 

ActionDave

Moderator
Staff member
If the circuit breaker panel is located outside and has a main breaker, can this main breaker serve as the above mentioned main service disco?
Yes. Pretty much a standard set up here where I live and has been that way for about forty years.
 

Strombea

Member
I think a pair of dykes to cut the poco meter tag and then simply pulling the meter is better than actual discos, most people put padlocks on Mains anyway so pulling meter is probably quicker
 

don_resqcapt19

Moderator
Staff member
I didn't say that.

Our industry has 50+ years of outdoor breaker installation history, particularly with multi-meter centers. I have no significant amount anecdotal evidence of outdoor breakers not offering appropriate protection except when they overheat in sunshine.
But I did say that and the manufactures publications are 110.3(B) instructions. Just because we have not had seen problems does not mean there is not a code violation.
 