I saw a remodel job today where the previous contractor left unfinished because he bankrupt 
The main panel was left empty so it needs to be rewired.
There is 3 meters from the service drop. Each meter has it is own old 60A main disconnect.
After doing some calc, one of the main disconnect is not going to cut it. It needs an 100A.
Can 2 main disconnect remains at 60A and one at 100A or do they all need to be the same?
Also the main disconnect that needs to be changed is not grounded but the panel has ground and neutral connected. Is that correct?
Just asking because the 2 other main disconnect are grounded but the panel they serve have neutral and ground separate.
The neutral are connected to th GE at the meter