I was told by a home owner that an electrician told him it was ok to install a sub panel in his attic as long as it was overcurrent protected by the main service panel located in the 1st floor of the home.
The home is a residential 1200 sf home, no basement and only 1 habitable floor. The panel that I saw in the attic is a 100amp main lug only panel accessible by a portable ladder fed with a 50amp 2 pole breeaker. The service is 100amp at the dwelling. The intent is to power additional circuits for the kitchen area and sub feed a panel in the detached garage from the attic located panel.
The temperature of the attic will get hot, very hot in the summer and I am wondering if I can get some input regarding any non compliance code issues regarding this installation. The head room in the attic is only 5 feet at most from the highest point in the attic. (ceiling joist to roof joist)
I am concerned about conductor deration, overcurrent device accessibility, premature tripping due to heat and working space requirements.
The only access to this attic is via a portable ladder. (not permanent).
Any time a breaker trips in this panel, it will be time to get the ladder out.
Can I get a bit of direction in identifying non compliance here for my own benefit?
So far article 110 is the direction I have started.
Thank You
The home is a residential 1200 sf home, no basement and only 1 habitable floor. The panel that I saw in the attic is a 100amp main lug only panel accessible by a portable ladder fed with a 50amp 2 pole breeaker. The service is 100amp at the dwelling. The intent is to power additional circuits for the kitchen area and sub feed a panel in the detached garage from the attic located panel.
The temperature of the attic will get hot, very hot in the summer and I am wondering if I can get some input regarding any non compliance code issues regarding this installation. The head room in the attic is only 5 feet at most from the highest point in the attic. (ceiling joist to roof joist)
I am concerned about conductor deration, overcurrent device accessibility, premature tripping due to heat and working space requirements.
The only access to this attic is via a portable ladder. (not permanent).
Any time a breaker trips in this panel, it will be time to get the ladder out.
Can I get a bit of direction in identifying non compliance here for my own benefit?
So far article 110 is the direction I have started.
Thank You