Towzzer
Does the NEC require in any situations that a sub-panel have a main? (i.e. lengh from main panel, number of circuits)
Re: Main on Subpanels
In general, as long as the sub-panel is in the same building as the power source the NEC does not require a main. Overcurrent protection for the sub-panel is required, but it does not have to be in the form of a main.
Don
added left out word
[ September 01, 2005, 01:59 PM: Message edited by: don_resqcapt19 ]
in any situations
This is why I replied yes it does. As Don points out, seperate buildings is where it can be required. Other requirements apply when multifamily dwellings have service disconects that are in locked rooms , and unavailable to the tenants.
Originally posted by macmikeman: Other requirements apply when multifamily dwellings have service disconnects that are in locked rooms , and unavailable to the tenants.
But even then you don't have to have a main on each tenant's panel, if the owner arranges for someone to be available 24/7/365 with a key to the room containing the individual disconnects.
So my answer would be "Yes, but only in very limited situations."
Can someone please clarify this.
Situation : Feeder to remote garage apartment ( multiwire )
Question : Is disconnect required at House, garage panel or BOTH ?
You need a disconnecting means at the garage. It can be a simple (i.e., non-fused)disconnecting switch on the outside. It could be a main breaker in the panel inside the garage.
You also need overcurrent protection for the feeder conductors from the house to the garage. This is usually done by having a circuit breaker in the house panel protect the feeder conductors to the garage.